Quote:
Originally Posted by DPete1104 View Post
I have a question....is it ok to set up the piping so that the regulator is inside the studio rather than outside on the tank? I would want to put it just past the inside cutoff valve. I'm using a barbeque tank..they will be putting a locked cage or box over it on the outside...this building is a "historical" structure so we are limited as to what we can do on the outside of the building
IF it is a secondary regulator........

NFPA code allows one to bring propane into residence at a maximum pressure of 10 PSI.....

So by putting a "fixed pressure" primary regulator set to 10PSI (MAX) at tank and then connecting a adjustable (secondary) regulator to piping to inside you can have a range of 0 to 10 psi in studio....

Other option may be to get "fixed" pressure regulator (for primary at tank) at maybe 2 or 5 PSI and save cost of adjustable regulator and just learn to work with torch at preset supply pressure....

Dale