Default When are flashback arrestors needed?

I have been using a torch since 2005 but am suddenly a bit confused about when flashback arrestors and check valves are needed. I have never used either of these things on my current setup which is a Mini CC with a 10 lpm concentrator and a propane tank with regulator. I’m getting ready to buy a new torch and want to make sure that I do things right. After doing some research, this is what I’m lead to believe:

Pre-mix torches MUST have flashback arrestors installed.

Surface mix torches don’t need flashback arrestors, but it is a good idea to have one installed on the fuel hose.

A flashback arrestor should not be used on an oxygen concentrator hose. Is this true even with a pre-mix torch?

Never even heard of a check valve until today. Are these necessary?

Can somebody clear things up for me please?
__________________
Lynn

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Reply With Quote
  #2  
Old 2013-09-19, 4:53pm
De Anza Art Glass Club De Anza Art Glass Club is offline
Senior Member
 
Join Date: Nov 24, 2009
Posts: 205
Default

I have a German burner (not a Herbert Arnold) that uses propane, oxygen, and air. The manufacturer recommends a check valve in the air line to prevent oxygen from backing up into the air supply line.

I would say that flashback arrestors are usually paired with check valves. Flashback occurs when the oxygen flows into the fuel line (and less frequently, when the fuel flows into the oxygen line, since oxygen pressures are generally higher than fuel pressures ... until the tank runs out). Check valves prevent the reverse flow of gas and flashback arrestors dissipate the heat of the flame flowing through them, so by that description, they both have a function in preventing a flashback from reaching the cylinders.

I would guess that a check valve would not be favored with an oxygen concentrator since it is an additional pressure drop.
Reply With Quote
  #3  
Old 2013-09-20, 4:34am
Dale M.'s Avatar
Dale M. Dale M. is offline
Gentleman of Leisure
 
Join Date: Jun 10, 2005
Location: A Little Bit West of Yosemite Valley
Posts: 5,200
Default

Careful with the terminology and how its used... A "flashback arrestor" is by nature a check valve.... And it does not stop the transfer of heat, it stops the reverse flow of gasses so they do not intermix and explode as a fame front travels back down hose (or torch body) ....

A "fire check" is constructed as a screen of porous materials that is dense enough the fuel gas (natural gas or propane) can flow through it at molecular level but a flame front can not pass through it.... And constructed differently then a check valve... And is generally used with natural gas supplies at levels local utility company supplies it at (pressure to low for gas pressure to open a "check valve" flashback arrestor)...

Dale
__________________
You can lead a person to knowledge, but you can't make them think.

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Vendor-Artist-Studio-Teacher Registry

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
San Francisco - A Few Toys Short of a Happy Meal

Last edited by Dale M.; 2013-09-21 at 6:47am.
Reply With Quote
  #4  
Old 2013-09-20, 10:08am
Silver Moon Lampwork's Avatar
Silver Moon Lampwork Silver Moon Lampwork is offline
Against the Grain
 
Join Date: Dec 07, 2006
Location: The Villages, FL
Posts: 1,398
Default

Thank you both for your input!
__________________
Lynn

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 
Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump




All times are GMT -7. The time now is 7:30am.


Powered by vBulletin® Version 3.7.5
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Your IP: 3.133.147.87