Default AIM kiln plugged into multi-plug?

I thought that kilns had to be plugged into the wall socket directly. One of my housemates put in one of those "multiplug" things for me (converting two sockets to six), because I was having to plug my oxygen concentrator in on the other side of the room and it was bugging him I guess (my studio space is in our shared garage and he has his work bench and drum kit in there). He doesn't see any reason why it wouldn't be safe... I don't know much/anything about electrical stuff and I thought I'd heard somewhere that kilns need to go directly into the wall.

So, is it safe to use the multiplug thing with it? Or not? It's not a question of overloading the circuit because our whole garage is on one circuit anyway and presumably all that stuff isn't overloading it.

I told him that I could just make a point of unplugging my oxycon and moving it out of his way every time I'm done in there but it would definitely be more convenient to just use the multi thing..
__________________

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Reply With Quote
  #2  
Old 2012-01-29, 8:54pm
Alaska Alaska is offline
Alaska Boro
 
Join Date: Dec 10, 2009
Location: Anchorage, Alaska
Posts: 1,065
Default

It is never good practice to place an appliance that takes high power either on an extension cord or on a "multiplug". Most household circuits are wired with number 12 copper wire. If the extension cord is number 12 and if the "multiplug" is wired for a 20 amp circuit the you could be OK..

However, if you want to be on the safe side, then the use of a duplex 110 volt 20 circuit would be in order. Keep in mind that kilns can take from 10 to 18 amps. And a concentrator perhaps 4 to 5 amps. It could be very easy to overload the circuit again depending on your kiln rating which was not stated.
Reply With Quote
  #3  
Old 2012-01-29, 8:55pm
Dale M.'s Avatar
Dale M. Dale M. is offline
Gentleman of Leisure
 
Join Date: Jun 10, 2005
Location: A Little Bit West of Yosemite Valley
Posts: 5,200
Default

Probable not a problem (just maybe not a good idea if its poorly rated) .... It's just a "receptacle".... The real issue is how much amperage draw is on single breaker supplying garage...

Dale
__________________
You can lead a person to knowledge, but you can't make them think.

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Vendor-Artist-Studio-Teacher Registry

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
San Francisco - A Few Toys Short of a Happy Meal
Reply With Quote
  #4  
Old 2012-01-30, 1:20am
amyhoust's Avatar
amyhoust amyhoust is offline
Senior Member
 
Join Date: Mar 04, 2007
Posts: 791
Default

Yeah and I think we are OK as far as that all goes. Haven't had any problems with blowing fuses or anything, so far.
__________________

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Reply With Quote
  #5  
Old 2012-01-30, 1:21am
amyhoust's Avatar
amyhoust amyhoust is offline
Senior Member
 
Join Date: Mar 04, 2007
Posts: 791
Default

I'm not sure what my kiln rating is, it is quite a small AIM bead kiln though...
__________________

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Reply With Quote
  #6  
Old 2012-01-30, 5:52am
laserglass's Avatar
laserglass laserglass is offline
old fart
 
Join Date: Apr 18, 2006
Location: st paul mn
Posts: 778
Default

most outlets and lights are daisy-chained off of a single breaker. you need a separate breaker for your kiln, and another breaker for your oxycon and everything else.
__________________
Mark Wilson

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Reply With Quote
  #7  
Old 2012-01-30, 10:55am
cheng076's Avatar
cheng076 cheng076 is offline
Curmudgeon Engineering
 
Join Date: Feb 15, 2006
Location: Near Seattle, WA
Posts: 1,723
Default

I find that here most houses have seperate circuits for lights, usually 15 amp service, and receptacles, sometimes 20 amp service; at least in more recent construction. When I did my place all circuits are 20 amp and only 4 receptacles on a circuit. I like having lots of power available. If it isn't popping the breaker then it's probably OK. Might mention that if a breaker pops alot it will weaken the breaker and it will start popping at less and less amps so you will have to change it out.
Reply With Quote
  #8  
Old 2012-02-03, 2:50pm
juba's Avatar
juba juba is offline
Junior Member
 
Join Date: Jan 16, 2012
Posts: 25
Default

I did that once and the cord from the plug strip MELTED to the wall socket..... NOT good ...do NOT recommend... The rating on most common plug strips is not high enough to run a kiln safely...imho. just plug it directly into the wall socket.. its safer...
__________________

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Reply With Quote
  #9  
Old 2012-02-03, 2:59pm
ewdb's Avatar
ewdb ewdb is offline
burnin' glass just becuz
 
Join Date: Apr 16, 2006
Location: Ottawa, Canada
Posts: 1,251
Default

i'd check you kiln booklet... mine specifically says DO NOT use with extension cords etc. so it remains plugged directly into the wall.
__________________
Evelyn - Carlisle Lucio w/ 8lpm EX-15
To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.

Give ideas away - there are new ones underneath... Diane Vreeland
Reply With Quote
  #10  
Old 2012-02-03, 4:51pm
PittsGlass's Avatar
PittsGlass PittsGlass is offline
Glass Hive Kiln Tech.
 
Join Date: Jun 23, 2007
Location: Toledo, OR
Posts: 907
Default

As a kiln manufacturer, I say that is not a safe situation. The power strips are just a thin strip of metal jumping all the plugs together. They can melt. You can have an unsafe draw without blowing a breaker in some circumstances. Even our Short Guy that draws only 8amps should be on its own circuit (a desk lamp would be ok, but nothing with a heater or a pump). Just think about how many space heater plugs start to melt in the outlet under heavy use. Loose outlets in the strips can also cause arcing of the plug to the strip, welding it together.

Be safe and drop another circuit in the room. We'd rather him be bothered than you be crispy.
__________________

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


It's not what you look at that matters, it's what you see.
Henry David Thoreau
Reply With Quote
  #11  
Old 2012-02-03, 8:55pm
Dale M.'s Avatar
Dale M. Dale M. is offline
Gentleman of Leisure
 
Join Date: Jun 10, 2005
Location: A Little Bit West of Yosemite Valley
Posts: 5,200
Default

Is this type of 6 outlet receptacle you "helper" put on outlet?



Also you really need more breakers service your work space....

Dale
__________________
You can lead a person to knowledge, but you can't make them think.

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Vendor-Artist-Studio-Teacher Registry

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
San Francisco - A Few Toys Short of a Happy Meal

Last edited by Dale M.; 2012-02-03 at 8:57pm.
Reply With Quote
  #12  
Old 2012-02-03, 10:34pm
amyhoust's Avatar
amyhoust amyhoust is offline
Senior Member
 
Join Date: Mar 04, 2007
Posts: 791
Default

That is the type Dale, yes.

Can someone explain why I need everything to be on separate breakers? I really know so little about electricity.
__________________

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Reply With Quote
  #13  
Old 2012-02-04, 5:19am
PerfectDeb's Avatar
PerfectDeb PerfectDeb is offline
Unmedicated since '62
 
Join Date: Jan 18, 2009
Location: Hunter Valley, Australia
Posts: 5,907
Default

Because the kiln draws a lot of power - nevertheless if the breakers are not tripping then it might not be an issue
__________________
Deb

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
- my 17yo sons first novel


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
- download, get organised, enjoy
Reply With Quote
  #14  
Old 2012-02-04, 11:58am
amyhoust's Avatar
amyhoust amyhoust is offline
Senior Member
 
Join Date: Mar 04, 2007
Posts: 791
Default

That's kind of what I was thinking Deb. Unless there is a safety reason to need to have it on a separate breaker.

I've been operating this setup for years too and never had a problem... although I know that doesn't always necessarily mean something is safe, it seems like there is enough power to run everything at least. The only thing different recently is the multiplug thing, which I am going to stop using cause you guys have made me sufficiently paranoid about that...
__________________

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Reply With Quote
  #15  
Old 2012-02-04, 8:09pm
Dale M.'s Avatar
Dale M. Dale M. is offline
Gentleman of Leisure
 
Join Date: Jun 10, 2005
Location: A Little Bit West of Yosemite Valley
Posts: 5,200
Default

The specs on those units (quality ones) are 15 amp... That is rating of receptacle its plugged into and probably rating of circuit breaker supplying receptacle.... If unit is does not get warm under full use its probably ok...

Dale
__________________
You can lead a person to knowledge, but you can't make them think.

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Vendor-Artist-Studio-Teacher Registry

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
San Francisco - A Few Toys Short of a Happy Meal
Reply With Quote
  #16  
Old 2012-02-05, 9:41am
LarryC LarryC is offline
Senior Member
 
Join Date: Mar 07, 2011
Location: Northern California
Posts: 2,023
Default

Quote:
Originally Posted by amyhoust View Post
That's kind of what I was thinking Deb. Unless there is a safety reason to need to have it on a separate breaker.

I've been operating this setup for years too and never had a problem... although I know that doesn't always necessarily mean something is safe, it seems like there is enough power to run everything at least. The only thing different recently is the multiplug thing, which I am going to stop using cause you guys have made me sufficiently paranoid about that...
There are quality electrical strips available that are suitable. You just have to read the rating when buying.
Reply With Quote
  #17  
Old 2012-02-05, 1:25pm
amyhoust's Avatar
amyhoust amyhoust is offline
Senior Member
 
Join Date: Mar 04, 2007
Posts: 791
Default

Is there a way to know what the rating is by looking at the thing? Like, is it written on there somewhere?
__________________

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Reply With Quote
  #18  
Old 2012-02-05, 3:08pm
Alaska Alaska is offline
Alaska Boro
 
Join Date: Dec 10, 2009
Location: Anchorage, Alaska
Posts: 1,065
Default

There should be a name plate that lists the current in amps and voltage rating. You will have to look and see where that is posted for your particular model. If that fails, then Google for your model number or if the firm is still in business call them.

The other option is to use any number of watt measuring devices. Perhaps kill a watt, energy saver or watts up would be appropriate for your needs. The next possibility would be use to a DMM or VOM to measure the cold resistance of the elements and then calculate the power using Ohm's Law.

If none of this fits into your needs, then arrange for a licensed electrician to determine what is appropriate.
Reply With Quote
  #19  
Old 2012-02-05, 7:35pm
Dale M.'s Avatar
Dale M. Dale M. is offline
Gentleman of Leisure
 
Join Date: Jun 10, 2005
Location: A Little Bit West of Yosemite Valley
Posts: 5,200
Default

Data should be printed on back of unit.... IF not, I would think its a cheap "Chinese Republic Authentic Product" (CRAP)...

Dale
__________________
You can lead a person to knowledge, but you can't make them think.

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Vendor-Artist-Studio-Teacher Registry

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
San Francisco - A Few Toys Short of a Happy Meal
Reply With Quote
  #20  
Old 2012-02-05, 9:33pm
LarryC LarryC is offline
Senior Member
 
Join Date: Mar 07, 2011
Location: Northern California
Posts: 2,023
Default

Quote:
Originally Posted by Dale M. View Post
Data should be printed on back of unit.... IF not, I would think its a cheap "Chinese Republic Authentic Product" (CRAP)...

Dale
100% right. Wouldnt trust it at all if it isnt clearly marked.
Reply With Quote
  #21  
Old 2012-02-05, 10:40pm
amyhoust's Avatar
amyhoust amyhoust is offline
Senior Member
 
Join Date: Mar 04, 2007
Posts: 791
Default

It actually is rated for 15 Amp.. would that mean it's safe to use? My kiln is 14 Amp but I guess the oxy con and possibly my laptop would be plugged in as well. Maybe two oxy cons in future if I get my second one working again.
__________________

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Reply With Quote
  #22  
Old 2012-02-06, 8:05am
Dale M.'s Avatar
Dale M. Dale M. is offline
Gentleman of Leisure
 
Join Date: Jun 10, 2005
Location: A Little Bit West of Yosemite Valley
Posts: 5,200
Default

The breaker that is powering it is probably 15 amp.... The receptacle that it is plugged into is probably 15 amp.... And if its has a "UL" approval sticker or marking...

The 6 outlet adapter is more civilized and replaces something like this....



Dale
__________________
You can lead a person to knowledge, but you can't make them think.

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Vendor-Artist-Studio-Teacher Registry

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
San Francisco - A Few Toys Short of a Happy Meal

Last edited by Dale M.; 2012-02-06 at 8:14am.
Reply With Quote
  #23  
Old 2012-02-07, 10:15am
cheng076's Avatar
cheng076 cheng076 is offline
Curmudgeon Engineering
 
Join Date: Feb 15, 2006
Location: Near Seattle, WA
Posts: 1,723
Default OMG

And in a bathroom!

It's so scary it made me laugh (nervously)
Reply With Quote
  #24  
Old 2012-02-12, 9:10pm
ozarkcat's Avatar
ozarkcat ozarkcat is offline
I'm listen-Oooh, sparkly!
 
Join Date: Jul 24, 2009
Location: Southwest Missouri Ozarks
Posts: 160
Default

Okay, as an explanation to make it make more sense:

Amperage is like water going through a pipe - a larger pipe represents a higher amperage, or capacity to carry water through it. If you have too much water (amps) going through a small pipe (wire, breaker or outlet), you blow out the pipes (flip breakers/can cause an electrical fire).

If you've got a 15 amp circuit, you can add items up being used at the same time for a total of 15 amps. So if your kiln is 14 amps, your concentrator is 4-6 amps, and your laptop draws maybe 1 amp (figuring 120 watts at 120 volts). If you're running them all at the same time on a 15 amp circuit, you're trying to run 20 amps through it and are risking throwing breakers.

Hope that helped and didn't just muddy the waters for you
__________________
Cat

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.

"Be the change you want to see in the world." Ghandi
Reply With Quote
  #25  
Old 2012-02-13, 10:52pm
cheng076's Avatar
cheng076 cheng076 is offline
Curmudgeon Engineering
 
Join Date: Feb 15, 2006
Location: Near Seattle, WA
Posts: 1,723
Default

Pretty good explanation. Now add that the voltage is like the water pressure that pushes it all through the pipe and that resistance is like.... wait for it..... resistance....LOL that tries to hold it back from flowing.
Reply With Quote
  #26  
Old 2012-02-14, 9:33am
Dale M.'s Avatar
Dale M. Dale M. is offline
Gentleman of Leisure
 
Join Date: Jun 10, 2005
Location: A Little Bit West of Yosemite Valley
Posts: 5,200
Default

Quote:
Originally Posted by cheng076 View Post
Pretty good explanation. Now add that the voltage is like the water pressure that pushes it all through the pipe and that resistance is like.... wait for it..... resistance....LOL that tries to hold it back from flowing.
Resistance is like putting thumb over end of hose.....

Dale
__________________
You can lead a person to knowledge, but you can't make them think.

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Vendor-Artist-Studio-Teacher Registry

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
San Francisco - A Few Toys Short of a Happy Meal
Reply With Quote
  #27  
Old 2012-02-14, 9:34am
amyhoust's Avatar
amyhoust amyhoust is offline
Senior Member
 
Join Date: Mar 04, 2007
Posts: 791
Default

Thanks guys The water analogy is actually quite helpful.
__________________

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump




All times are GMT -7. The time now is 8:44pm.


Powered by vBulletin® Version 3.7.5
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Your IP: 3.17.6.75