Post Ventilation - connecting to existing exhaust

My first post! I'm new to lampworking and all the posts on ventilation have been so helpful, but I didn't see anyone address my particular question.

I have an exhaust fan (just 80 cfm) in my studio already that vents out through the roof and I just got the 650 CFM exhaust hood from Glasscraft, Inc.

Can I chain these together or will that restrict the CFM from the hood? Basically, do I need to rip out the existing fan?

Thanks!

Joann
Reply With Quote
  #2  
Old 2005-12-05, 6:46am
MikeAurelius's Avatar
MikeAurelius MikeAurelius is offline
Safety ALWAYS
 
Join Date: Jun 10, 2005
Location: Sauk Rapids, Minnesota
Posts: 2,401
Default

No. Don't do this. Most likely the existing fan does not have a large enough duct size to handle the larger air movement of the new fan.

Additionally, because the original fan is so "small", even if it was running, the new fan would actually force air past the other fan, causing recycling of the exhaust plume.

When you have multiple fans, you need multiple exhaust ducts.

Don't forget, with the larger fan, you are also going to need a larger source of fresh replacement air.
__________________

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


Chaotic Glass: Safety for the glassworker, and random thoughts and opinions on the state of the glassworking world
To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Reply With Quote
  #3  
Old 2005-12-05, 4:43pm
Joann Joann is offline
Junior Member
 
Join Date: Sep 18, 2005
Posts: 6
Default

Ah, it figures. Glad I asked first before trying it! I think I'll do a window setup to vent to the outside.

I do have a crawlspace so I could theoretically try to do setup similar to yours to have a vent in the table for replacement air, but that would be too close to the vent going outside, right?

Maybe I'll just open the window in another room.

Thanks so much for your help!
Reply With Quote
  #4  
Old 2005-12-06, 8:12am
MikeAurelius's Avatar
MikeAurelius MikeAurelius is offline
Safety ALWAYS
 
Join Date: Jun 10, 2005
Location: Sauk Rapids, Minnesota
Posts: 2,401
Default

Replacement air "source" has to be a minimum of 10 feet from the exhuast duct. It's always best to duct the replacement air - if you don't you risk drawdown of the air pressure in the entire house, which can have some unpleasant results, the least of which is a sewer smell from the plumbing vents...
__________________

To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.


Chaotic Glass: Safety for the glassworker, and random thoughts and opinions on the state of the glassworking world
To view links or images in signatures your post count must be 5 or greater. You currently have 0 posts.
Reply With Quote
Reply


Currently Active Users Viewing This Thread: 1 (0 members and 1 guests)
 

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Forum Jump




All times are GMT -7. The time now is 5:39am.


Powered by vBulletin® Version 3.7.5
Copyright ©2000 - 2024, Jelsoft Enterprises Ltd.
Your IP: 18.223.0.53